[ Log In ]
[ Register ]

Question #: 13789

Question: how to conect the VFD spindle using modbus

Current Solution

It is possible to connect and configure the spindle VFD to the mach3 via an RS485 communication and protocol.

The first thing you will need is the dynamic link library to pair with mach3 called the Huanyang VFD Mach3 PlugIn. You can find this file at the mach3 support forum here: http://www.machsupport.com/forum/index.php/topic,14182.0.html

You will also need to download the Microsoft .net 3.5 framework and install it: https://www.microsoft.com/en-us/download/details.aspx?id=21

Follow the pdf that comes with the library file, but here is a synopsis of what you need to do (I also added a lot more information that may be useful during this process as the manual does not cover the main connections that need to be done):

You will need to program your VFD so that it knows how to communicate with mach3 and the computer (go into the programming mode of the VFD and change these parameters):
- PD001 - value 2 - Enables with communication aspect of the VFD
- PD002 - value 2 - Enables frequency control from the communcations port
- PD163 - value 1 - VFD address
- PD164 - value 1 - Baud rate of 9600 (speed of the communication)
- PD165 - value 3 - 8N1 RTU - 8 bits (that's the size of the word that gets communicated), N (No parity or no error checking) and 1 (1 stop bit)

Copy the dll file to the PlugIns folder of mach3.

Connect the RX and TX lines to your computer. There are a couple ways you can do this, but the recommended way would be to use an FTDI USB device which converts a USB to a serial com port. The device will have Rx and Tx connectors to connect to the VFD terminals with the same labels. This method is recommended since serial ports are not as common in computers these days.

Next, you will need to configure mach3 to use the plugin library. Start mach3 and click on Menu -> config ->Config Plugins. Enable the new plugin by clicking on the red cross on the left column next to the plug in. Restart mach3 after doing this.

No you need to configure mach3 to use the HuanyangVFD plugin. Go to the ports & pins configuration and select the spindle setup tab. Make sure that the Disable Spindle Relays checkbox is unchecked. We don't want mach3 to output a signal for a relay since the spindle will start up and turn off within the VFD and not from an external relay.

Next, go to the HuanyangVFD settings by clicking on Menu -> plugin control -> HuanyangVFD. Set the parameters to the same settings you put into the VFD programming. The com port will be shown as new hardward when you plug in the USB FTDI device. A little bubble will be displayed at the bottom right where it will notify you that a new device is being installed (be patient while windows assigns a com port). Alternatively, you can use the windows device manager to see which port was set for the new USB FTDI device). You may need to restart mach3 several times until you get the correct information displayed in the PD001 and PD002 fields. When the com port is correct and the other parameters, like baud and VFD address is the same as you entered in the programming, then the PD001 and PD002 will show the number 2, otherwise, a 99 will appear which means that communication was not successful.

You can now control the on/off and RPM of the spindle using the RS485 communication between mach3 and the VFD.

Additional Information:
Will this work with the brand called "best "vfd as well.

Additional Information:
Where Can i find vfd plug-in for yl-620a for mach3 MODBUS?

Additional Information:
Once you connect the RS485 to MAch 3 and make all the connections, will MAch 3 automatically turn the spindle on when you start a cut file?

Respond:

Other Possible Solutions to this Question

  • how to conect the VFD spindle using modbus

    It is possible to connect and configure the spindle VFD to the mach3 via an RS485 communication and protocol.

    The first thing you will need is the dynamic link library to pair with mach3 called the Huanyang VFD Mach3 PlugIn. You can find this file at the mach3 support forum here: http://www.machsupport.com/forum/index.php/topic,14182.0.html

    You will also need to download the Microsoft .net 3.5 framework and install it: https://www.microsoft.com/en-us/download/details.aspx?id=21

    Follow the pdf that comes with the library file, but here is a synopsis of what you need to do (I also added a lot more information that may be useful during this process as the manual does not cover the main connections that need to be done):

    You will need to program your VFD so that it knows how to communicate with mach3 and the computer (go into the programming mode of the VFD and change these parameters):
    - PD001 - value 2 - Enables with communication aspect of the VFD
    - PD002 - value 2 - Enables frequency control from the communcations port
    - PD163 - value 1 - VFD address
    - PD164 - value 1 - Baud rate of 9600 (speed of the communication)
    - PD165 - value 3 - 8N1 RTU - 8 bits (that's the size of the word that gets communicated), N (No parity or no error checking) and 1 (1 stop bit)

    Copy the dll file to the PlugIns folder of mach3.

    Connect the RX and TX lines to your computer. There are a couple ways you can do this, but the recommended way would be to use an FTDI USB device which converts a USB to a serial com port. The device will have Rx and Tx connectors to connect to the VFD terminals with the same labels. This method is recommended since serial ports are not as common in computers these days.

    Next, you will need to configure mach3 to use the plugin library. Start mach3 and click on Menu -> config ->Config Plugins. Enable the new plugin by clicking on the red cross on the left column next to the plug in. Restart mach3 after doing this.

    No you need to configure mach3 to use the HuanyangVFD plugin. Go to the ports & pins configuration and select the spindle setup tab. Make sure that the Disable Spindle Relays checkbox is unchecked. We don't want mach3 to output a signal for a relay since the spindle will start up and turn off within the VFD and not from an external relay.

    Next, go to the HuanyangVFD settings by clicking on Menu -> plugin control -> HuanyangVFD. Set the parameters to the same settings you put into the VFD programming. The com port will be shown as new hardward when you plug in the USB FTDI device. A little bubble will be displayed at the bottom right where it will notify you that a new device is being installed (be patient while windows assigns a com port). Alternatively, you can use the windows device manager to see which port was set for the new USB FTDI device). You may need to restart mach3 several times until you get the correct information displayed in the PD001 and PD002 fields. When the com port is correct and the other parameters, like baud and VFD address is the same as you entered in the programming, then the PD001 and PD002 will show the number 2, otherwise, a 99 will appear which means that communication was not successful.

    You can now control the on/off and RPM of the spindle using the RS485 communication between mach3 and the VFD.

    Additional Information:
    Will this work with the brand called "best "vfd as well.

    Additional Information:
    Where Can i find vfd plug-in for yl-620a for mach3 MODBUS?

    Additional Information:
    Once you connect the RS485 to MAch 3 and make all the connections, will MAch 3 automatically turn the spindle on when you start a cut file?

    Click the link to add information to this solution:
    how to conect the VFD spindle using modbus

  • How to connect the spindle VFD to RS-485 serial modbus

    It is possible to connect and configure the spindle VFD to the mach3 via an RS485 communication and protocol.

    The first thing you will need is the dynamic link library to pair with mach3 called the Huanyang VFD Mach3 PlugIn. You can find this file at the mach3 support forum here: http://www.machsupport.com/forum/index.php/topic,14182.0.html

    You will also need to download the Microsoft .net 3.5 framework and install it: https://www.microsoft.com/en-us/download/details.aspx?id=21

    Follow the pdf that comes with the library file, but here is a synopsis of what you need to do (I also added a lot more information that may be useful during this process as the manual does not cover the main connections that need to be done):

    You will need to program your VFD so that it knows how to communicate with mach3 and the computer (go into the programming mode of the VFD and change these parameters):
    - PD001 - value 2 - Enables with communication aspect of the VFD
    - PD002 - value 2 - Enables frequency control from the communcations port
    - PD163 - value 1 - VFD address
    - PD164 - value 1 - Baud rate of 9600 (speed of the communication)
    - PD165 - value 3 - 8N1 RTU - 8 bits (that's the size of the word that gets communicated), N (No parity or no error checking) and 1 (1 stop bit)

    Copy the dll file to the PlugIns folder of mach3.

    Connect the RX and TX lines to your computer. There are a couple ways you can do this, but the recommended way would be to use an FTDI USB device which converts a USB to a serial com port. The device will have Rx and Tx connectors to connect to the VFD terminals with the same labels. This method is recommended since serial ports are not as common in computers these days.

    Next, you will need to configure mach3 to use the plugin library. Start mach3 and click on Menu -> config ->Config Plugins. Enable the new plugin by clicking on the red cross on the left column next to the plug in. Restart mach3 after doing this.

    No you need to configure mach3 to use the HuanyangVFD plugin. Go to the ports & pins configuration and select the spindle setup tab. Make sure that the Disable Spindle Relays checkbox is unchecked. We don't want mach3 to output a signal for a relay since the spindle will start up and turn off within the VFD and not from an external relay.

    Next, go to the HuanyangVFD settings by clicking on Menu -> plugin control -> HuanyangVFD. Set the parameters to the same settings you put into the VFD programming. The com port will be shown as new hardward when you plug in the USB FTDI device. A little bubble will be displayed at the bottom right where it will notify you that a new device is being installed (be patient while windows assigns a com port). Alternatively, you can use the windows device manager to see which port was set for the new USB FTDI device). You may need to restart mach3 several times until you get the correct information displayed in the PD001 and PD002 fields. When the com port is correct and the other parameters, like baud and VFD address is the same as you entered in the programming, then the PD001 and PD002 will show the number 2, otherwise, a 99 will appear which means that communication was not successful.

    You can now control the on/off and RPM of the spindle using the RS485 communication between mach3 and the VFD.

    Additional Information:
    Will this work with the brand called "best "vfd as well.

    Additional Information:
    Where Can i find vfd plug-in for yl-620a for mach3 MODBUS?

    Additional Information:
    Once you connect the RS485 to MAch 3 and make all the connections, will MAch 3 automatically turn the spindle on when you start a cut file?

    Click the link to add information to this solution:
    How to connect the spindle VFD to RS-485 serial modbus

  • How do I conect the VFD of the spindle to the RS485 connections

    It is not necessary to connect the spindle VFD (Variable Frequency Drive also called an Inverter) to the computer or CNC motion electronics. The VFD can be controlled independently using the control panel on the VFD. The control panel has the ability to control all aspects of the spindle including Speed, Torque, limits, etc. However, you can connect the VFD to the computer so the CNC control program can control the spindle during the CNC Machine operation. You will need to connect the VFD to the computer via a serial conection (in this case, it is the RS-485 protocol).

    The following are instructions on how to connect the VFD to Mach3 via this RS-485 serial connection.

    The first thing you will need is the dynamic link library to pair with mach3 called the Huanyang VFD Mach3 PlugIn. You can find this file at the mach3 support forum here: http://www.machsupport.com/forum/index.php/topic,14182.0.html

    You will also need to download the Microsoft .net 3.5 framework and install it: https://www.microsoft.com/en-us/download/details.aspx?id=21

    Follow the pdf that comes with the library file, but here is a synopsis of what you need to do (I also added a lot more information that may be useful during this process as the manual does not cover the main connections that need to be done):

    You will need to program your VFD so that it knows how to communicate with mach3 and the computer (go into the programming mode of the VFD and change these parameters):
    - PD001 - value 2 - Enables with communication aspect of the VFD
    - PD002 - value 2 - Enables frequency control from the communcations port
    - PD163 - value 1 - VFD address
    - PD164 - value 1 - Baud rate of 9600 (speed of the communication)
    - PD165 - value 3 - 8N1 RTU - 8 bits (that's the size of the word that gets communicated), N (No parity or no error checking) and 1 (1 stop bit)

    Copy the dll file to the PlugIns folder of mach3.

    Connect the RX and TX lines to your computer. There are a couple ways you can do this, but the recommended way would be to use an FTDI USB device which converts a USB to a serial com port. The device will have Rx and Tx connectors to connect to the VFD terminals with the same labels. This method is recommended since serial ports are not as common in computers these days.

    Next, you will need to configure mach3 to use the plugin library. Start mach3 and click on Menu -> config ->Config Plugins. Enable the new plugin by clicking on the red cross on the left column next to the plug in. Restart mach3 after doing this.

    No you need to configure mach3 to use the HuanyangVFD plugin. Go to the ports & pins configuration and select the spindle setup tab. Make sure that the Disable Spindle Relays checkbox is unchecked. We don't want mach3 to output a signal for a relay since the spindle will start up and turn off within the VFD and not from an external relay.

    Next, go to the HuanyangVFD settings by clicking on Menu -> plugin control -> HuanyangVFD. Set the parameters to the same settings you put into the VFD programming. The com port will be shown as new hardward when you plug in the USB FTDI device. A little bubble will be displayed at the bottom right where it will notify you that a new device is being installed (be patient while windows assigns a com port). Alternatively, you can use the windows device manager to see which port was set for the new USB FTDI device). You may need to restart mach3 several times until you get the correct information displayed in the PD001 and PD002 fields. When the com port is correct and the other parameters, like baud and VFD address is the same as you entered in the programming, then the PD001 and PD002 will show the number 2, otherwise, a 99 will appear which means that communication was not successful.

    You can now control the on/off and RPM of the spindle using the RS485 communication between mach3 and the VFD.

    Additional Information:
    The question was how to connect the spindle to the redfy. I did not receive a VFD.
    I have the redFly system and a 2.2kW Spindle - 110V how do i connect the spindle?

    Additional Information:
    If you received a spindle without a VFD, please contact us asap. Our spindle will not work without a VFD.

    Additional Information:
    Hi, how is this setup in mach4?

    Click the link to add information to this solution:
    How do I conect the VFD of the spindle to the RS485 connections

  • HOW DO YOU HOOK UP THE VFD TO SPINDLE?

    U - Pin1
    V - Pin2
    W - Pin3
    Pin4 Dead

    Additional Information:
    My home made cnc is a big problem with my NC connection. When in start my spindle it will be gone wrong. It will be limith switch problem anytime. Need help thanks.

    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    HOW DO YOU HOOK UP THE VFD TO SPINDLE?

  • How do you connect the spindle VFD to the parallel breakout board

    The parallel board contains a relay that is connected to pin #16. You can use this relay as the start/stop by connecting the relay to the FOR and it's related digital GND pin on the VFD.

    Additional Information:


    Additional Information:


    Additional Information:


    Additional Information:

    Click the link to add information to this solution:
    How do you connect the spindle VFD to the parallel breakout board

  • HOW DO YOU SETUP THE SPINDLE INVERTER VFD?

    Change PD001 Source of Run Commands to '1'
    Change PD005 Max operating frequency to 400hz
    Change PD004 base frequency to 400hz
    Change PD003 Main frequency to 400hz
    Change PD006 Intermediate frequency to 2.5
    Change PD008 max voltage to 220v
    Change PD009 Intermediate voltage to 15v
    Change PD010 Min voltage to 8
    Change PD011 frequency lower limit to >100hz (120hz to start)
    Change PD142 7 Amps
    Change PD143 2
    Change PD144 3000

    Note: PD001 had to be changed back to 0 to allow for keypad control.
    Note2: I had to reverse U and V to get the spindle to go forward in FWD. (reverse any two wires, u&v or w&v for example)

    Additional Information:

    Click the link to add information to this solution:
    HOW DO YOU SETUP THE SPINDLE INVERTER VFD?

  • how much does the 2.2kW spindle and the VFD weigh together?

    The weight of the 2.2kW spindle without the VFD (variable frequency drive or inverter) is 11 lbs or 5 kg.

    The 2.2kW spindle with the VFD is 15 lbs or 6.8 kg.

    Additional Information:

    Click the link to add information to this solution:
    how much does the 2.2kW spindle and the VFD weigh together?

  • HOW DO YOU HOOK UP THE SPINDLE TO INVERTER?

    U - Pin1
    V - Pin2
    W - Pin3
    Pin4 Dead

    Additional Information:
    My home made cnc is a big problem with my NC connection. When in start my spindle it will be gone wrong. It will be limith switch problem anytime. Need help thanks.

    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    HOW DO YOU HOOK UP THE SPINDLE TO INVERTER?

  • How to display RPM instead of frequency on the VFD? I have the 2.2kv 110 volt spindle and inverter.

    There is a button on the front of the VFD that will cycle through RPM, Freq, and a few other readings. If there is a >> button on your VFD, that will work. If there is a mode button on your VFD, that should works as well.

    Additional Information:
    There is a >> disc button but it does not cycle through the display modes.

    Additional Information:
    Is there a parameter setting to make this button work to cycle thru the display modes?

    Additional Information:
    setting the starting rpm

    Additional Information:
    the vfd will not start the motor

    Additional Information:
    Any progress on this? I have the same issue.

    Additional Information:
    What model is your VFD?

    Additional Information:
    Mine is a YL620-G-5.5Kw

    Additional Information:
    That model will not be able to show RPM. You will be able to show the frequency, which can be used to determine the RPM. RPM equals the Frequency x 60.

    Additional Information:
    There is an Icon for RPM at the top of the display I cannot cycle through the different options to see the RPM

    Additional Information:
    At the top of my control panel is has 6 different lights which indicate what your seeing. in order from left to right they are COM, ALM, DISP, RUN, Hz, RPM I have seen the ALM light up on initial set up but that was fixes with a parameter change. The run light shows up when i turn the spindle on and and it is running. I am however not able to get any of the other lights to show or to get the RPMs to display

    Additional Information:
    If you do see an RPM light on the display, that panel sticker may be a sticker used for many types of VFDs and the RPM is not used. There is parameter: P00.24 which allows you to pick what to display. The choices a
    re:
    0: Display current target frequency. This will display your knobs, potentiometer, setting, not the actual spindle frequency.
    1: Display electric machinery run frequency. This will display the actual frequency that the VFD is currently sending to the spindle.
    2: Display electric machinery run current: this will display the current the spindle is currently drawing.
    3: Display input AC voltage. Self explanatory.
    4: Display mother line voltage. This will display the actual voltage at the input.
    5: Display output voltage. This will display the voltage at the UVW terminals for the spindle.
    6: Display speed paragraph number SPx. I believe this displays which frequency is being selected (P07.00 to P07.07, or 1 to 8 respectively).
    7: Display inverter temperature. This is the temp of the VFD, self explanatory.
    8: Display input signal X1-X3/output signal. This simply shows the inputs/outputs associated with the external terminals.
    9: Display user variable. This one I have not delved into, so it may be something to look into.
    10: Display user count value. Same, this one could be useful.
    11: Display temporary debugging variable. Haven't tried this one, so I can't inform of any useful information but it won't pertain to this subject anyway.
    12: Display automatic multisegment run step and time. I haven't delved into this one either, but it won't show RPM.

    Click the link to add information to this solution:
    How to display RPM instead of frequency on the VFD? I have the 2.2kv 110 volt spindle and inverter.

  • HOW TO CONNECT THE SPINDLE INVERTER?

    U - Pin1
    V - Pin2
    W - Pin3
    Pin4 Dead

    Additional Information:
    My home made cnc is a big problem with my NC connection. When in start my spindle it will be gone wrong. It will be limith switch problem anytime. Need help thanks.

    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    HOW TO CONNECT THE SPINDLE INVERTER?

  • What size of wire do you use to connect the VFD to the spindle?

    The type of wire that should be used between the spindle and the VFD (Variable Frequency Driver also called the inverter) should be of stranded type and we use between 18 and 16 AWG.

    The total current is divided among the three coil wires, therefor a wire gauge of 16 should be sufficient.

    Currently we use 20AWG 4 conductor.

    Additional Information:


    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    What size of wire do you use to connect the VFD to the spindle?

  • HOW MUCH SILICONE TUBE DO I NEED FOR A GREEN LEAN TO CONNECT THE SPINDLE

    The greenlean requires 56 feet of 1/4 Inside Diameter and 3/8 Outside Diameter silicon tube for the spindle.

    Additional Information:
    20

    Additional Information:
    20

    Click the link to add information to this solution:
    HOW MUCH SILICONE TUBE DO I NEED FOR A GREEN LEAN TO CONNECT THE SPINDLE

  • How to configure 2.2KW VFD for Modbus communication with Mach3

    It is possible to connect and configure the spindle VFD to the mach3 via an RS485 communication and protocol.

    The first thing you will need is the dynamic link library to pair with mach3 called the Huanyang VFD Mach3 PlugIn. You can find this file at the mach3 support forum here: http://www.machsupport.com/forum/index.php/topic,14182.0.html

    You will also need to download the Microsoft .net 3.5 framework and install it: https://www.microsoft.com/en-us/download/details.aspx?id=21

    Follow the pdf that comes with the library file, but here is a synopsis of what you need to do (I also added a lot more information that may be useful during this process as the manual does not cover the main connections that need to be done):

    You will need to program your VFD so that it knows how to communicate with mach3 and the computer (go into the programming mode of the VFD and change these parameters):
    - PD001 - value 2 - Enables with communication aspect of the VFD
    - PD002 - value 2 - Enables frequency control from the communcations port
    - PD163 - value 1 - VFD address
    - PD164 - value 1 - Baud rate of 9600 (speed of the communication)
    - PD165 - value 3 - 8N1 RTU - 8 bits (that's the size of the word that gets communicated), N (No parity or no error checking) and 1 (1 stop bit)

    Copy the dll file to the PlugIns folder of mach3.

    Connect the RX and TX lines to your computer. There are a couple ways you can do this, but the recommended way would be to use an FTDI USB device which converts a USB to a serial com port. The device will have Rx and Tx connectors to connect to the VFD terminals with the same labels. This method is recommended since serial ports are not as common in computers these days.

    Next, you will need to configure mach3 to use the plugin library. Start mach3 and click on Menu -> config ->Config Plugins. Enable the new plugin by clicking on the red cross on the left column next to the plug in. Restart mach3 after doing this.

    No you need to configure mach3 to use the HuanyangVFD plugin. Go to the ports & pins configuration and select the spindle setup tab. Make sure that the Disable Spindle Relays checkbox is unchecked. We don't want mach3 to output a signal for a relay since the spindle will start up and turn off within the VFD and not from an external relay.

    Next, go to the HuanyangVFD settings by clicking on Menu -> plugin control -> HuanyangVFD. Set the parameters to the same settings you put into the VFD programming. The com port will be shown as new hardward when you plug in the USB FTDI device. A little bubble will be displayed at the bottom right where it will notify you that a new device is being installed (be patient while windows assigns a com port). Alternatively, you can use the windows device manager to see which port was set for the new USB FTDI device). You may need to restart mach3 several times until you get the correct information displayed in the PD001 and PD002 fields. When the com port is correct and the other parameters, like baud and VFD address is the same as you entered in the programming, then the PD001 and PD002 will show the number 2, otherwise, a 99 will appear which means that communication was not successful.

    You can now control the on/off and RPM of the spindle using the RS485 communication between mach3 and the VFD.



    Additional Information:
    This looks easy enough, however, the VFD that came with my spindle is made by Huajiang, not a Huanyang. The parameter codes are different and do not line up with the ones offered in this response.

    Click the link to add information to this solution:
    How to configure 2.2KW VFD for Modbus communication with Mach3

  • HOW DO YOU SETUP THE SPINDLE INVERTER?

    Change PD001 Source of Run Commands to '1'
    Change PD005 Max operating frequency to 400hz
    Change PD004 base frequency to 400hz
    Change PD003 Main frequency to 400hz
    Change PD006 Intermediate frequency to 2.5
    Change PD008 max voltage to 220v
    Change PD009 Intermediate voltage to 15v
    Change PD010 Min voltage to 8
    Change PD011 frequency lower limit to >100hz (120hz to start)
    Change PD142 7 Amps
    Change PD143 2
    Change PD144 3000

    Note: PD001 had to be changed back to 0 to allow for keypad control.
    Note2: I had to reverse U and V to get the spindle to go forward in FWD. (reverse any two wires, u&v or w&v for example)

    Additional Information:

    Click the link to add information to this solution:
    HOW DO YOU SETUP THE SPINDLE INVERTER?

  • Good morning, I would like to know if the strength of the 2.2kw spindle is weaker when using the 110V version of the VFD. Does it have the same power as the 220V version VFD?

    The 2.2kW spindle will have the same amount of torque and strength using either the 110V or the 220V inverter. Nothing will significantly change in either application since the 110V inverter has a small step up transformer which will increase the voltage from 110V to 220V to run the spindle efficiently.

    Additional Information:
    I'd like confirmation on this -- isn't there a cost in efficiency to having the 110v step up to 220v?

    Additional Information:
    Thank you so very much for explaining this!!! I truly appreciate your help! Tricia

    Additional Information:
    Thank you so very much for explaining this!!! I truly appreciate your help! Tricia

    Additional Information:
    Thank you so very much for explaining this!!! I truly appreciate your help! Tricia

    Additional Information:
    Thank you so very much for explaining this!!! I truly appreciate your help! Tricia

    Additional Information:
    Thank you so very much for explaining this!!! I truly appreciate your help! Tricia

    Click the link to add information to this solution:
    Good morning, I would like to know if the strength of the 2.2kw spindle is weaker when using the 110V version of the VFD. Does it have the same power as the 220V version VFD?

  • HOW TO CONTROL MY 2.2 KW SPINDLE VIA MACH3

    You can go to our instructions on for the breakout board here: http://www.buildyourcnc.com/item/electronicsAndMotors-parallel-breakout-relay to get the information on turning the spindle on and off from the computer and mach3. Alternatively, you can connect the computer using RS485 serial to the inverter and send control commands that way.

    Additional Information:
    HOW TO CONTROL MY 2.2 KW SPINDLE VIA MACH3 usb

    Additional Information:


    Additional Information:


    Additional Information:
    How should I wire the Mach3 card (red, 4 axis) and the vfd (Yl620-a)?

    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    HOW TO CONTROL MY 2.2 KW SPINDLE VIA MACH3

  • What brand is the 2.2 kW spindle? Same for the VFD. Thanks.

    Spindles are generally covered up to 1 year after date of purchase. We do not repair them in house, but we do work with our manufacturer to replace defective units. Generally if you have a defective unit covered under warranty, we will issue a replacement.

    Click the link to add information to this solution:
    What brand is the 2.2 kW spindle? Same for the VFD. Thanks.

  • What wire size to use from VFD to 2.2kW spindle?

    We use 16 AWG wires between the spindle and the VFD. This wire size has a maximum capacity for 22 Amps, a good buffer to eliminate any possibility for overheating. The 2.2kW using 220V may draw up to 10 Amps (220 x 10 = 2200).

    That is, all three wires are sharing the total current draw.

    Additional Information:


    Additional Information:


    Additional Information:
    grounding a spindle


    Additional Information:

    Click the link to add information to this solution:
    What wire size to use from VFD to 2.2kW spindle?

  • I’M LOOKING TO PURCHASE SPINDLE AND VFD WAS CURIOS IF THE SPINDLES COME WITH COLLETS SO WHICH ONES?

    Yes, all of the spindles come with collets. The collets have a 1/4" (6.35mm) bore for end mills that have a 1/4" shank. The ER specification is different for the 1.5kW (ER-11) and the 2.2kW (ER-20).

    Additional Information:



    Additional Information:



    Additional Information:

    Click the link to add information to this solution:
    I’M LOOKING TO PURCHASE SPINDLE AND VFD WAS CURIOS IF THE SPINDLES COME WITH COLLETS SO WHICH ONES?

Get Help with:
This Product
Orders
Tech Support
Sales
This Product
Order Query
Tech Support
Sales
Not logged in. Log In Register
Track Order(s)
View Order(s)
I Want to Schecule a One-On-One Paid Tech Support Session
Book an Appointment Pertaining to a BuildYourCNC Product (Free)
Ask a Quesion Below (Free):
Book an Appointment Pertaining Other Equipment ($60/half hour)
Book an Immedite Appointment Pertaining Other Equipment ($120/half hour)
Ask a Quesion Below (Free):
Waiting for response... I may not answer immediately, but I was notified on my cellular phone so my response is forthcoming. If I don't respond immediately, you can always go to the [My Account] page to see all of our chats at any time.